What I meant was the Delta flow from the most demanding head was 1.25gpm.The actual flow from the head was 8.68gpm and the required flow was 7.43gpm which was a delta flow of 1.25gpm. My HydraCalc program refers to it as Delta Flow ( past experience I heard it being referred to as overage, would that be the correct term? I had a pressure of 170psi so my only concern was keeping the flow down for the meter size.
Thanks, George Medina Jr. -----Original Message----- From: Thom McMahon <tmcma...@firetechinc.com> To: sprinklerforum@firesprinkler.org Sent: Mon, Jul 20, 2009 8:38 am Subject: RE: Room design method - Technical information 1.5Gpm from a 2.8K is less than 1 Psi, you'd still need to meet the 7 Psi min. head pressure so even 2.8K heads would flow 7.41 Gpm+. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: Re: Room design method - Technical information My preliminary calculations worked out good with the delta flow not exceeding more than 1.5gpm using 2.8k heads covering 74 sq ft each _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: techsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: techsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)