See 3.2.3 in the 2007 edition.  Definition of listed says "Equipment, materials 
or services included in a list published by an organization acceptable to the 
AHJ ..."  If the AHJ accepts FM, then the product is listed with a lower case 
"L".  UL Listed is upper case.  13, etc. use the lower case version.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Thu, 7/23/09, Forest Wilson <[email protected]> wrote:


From: Forest Wilson <[email protected]>
Subject: Sprinkler listing
To: "Forum" <[email protected]>
Date: Thursday, July 23, 2009, 1:48 PM


If a product is FM approved, but not UL listed, does the FM approval satisfy 
the listing requirement?
NFPA does not require UL listing, but does require listing of sprinklers. (as I 
recall). 
I received a flyer for flexible heads, but they are not UL listed they are FM 
approved. 
Forest Wilson                  Project Manager               Cherokee Fire 
Protection Co. 1855 Bellbrook Ave. Ste C   Xenia OH 45385              
888-347-3079 ph             614-455-4324 fx           
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to