See 3.2.3 in the 2007 edition. Definition of listed says "Equipment, materials or services included in a list published by an organization acceptable to the AHJ ..." If the AHJ accepts FM, then the product is listed with a lower case "L". UL Listed is upper case. 13, etc. use the lower case version.
Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated 2715 Harrison St. Evanston, IL 60201 Tel: 847-733-0944 Fax: 847-866-6255 --- On Thu, 7/23/09, Forest Wilson <[email protected]> wrote: From: Forest Wilson <[email protected]> Subject: Sprinkler listing To: "Forum" <[email protected]> Date: Thursday, July 23, 2009, 1:48 PM If a product is FM approved, but not UL listed, does the FM approval satisfy the listing requirement? NFPA does not require UL listing, but does require listing of sprinklers. (as I recall). I received a flyer for flexible heads, but they are not UL listed they are FM approved. Forest Wilson Project Manager Cherokee Fire Protection Co. 1855 Bellbrook Ave. Ste C Xenia OH 45385 888-347-3079 ph 614-455-4324 fx _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)