Would a Potter PS40 connected to the building fire alarm system via a
monitor module not satisfy those requirements?

Ben Young

On Tue, Aug 11, 2009 at 1:27 PM, Mark Gouveia <[email protected]>wrote:

> I have a government project with a spec calling for a "Low Air Pressure
> Alarm Device" and want to pick the forum's brain to see if they have run
> across this before.  They want box with a buzzer and green (all ok), red
> (low air pressure), and amber (silence switch on) lights connected to a low
> air pressure switch.  See end of email for the exact language.
>
> I found a product that is close to the spec, but missing an amber light at
> http://www.modsafe.com/low%20pressure%20warning.htm .  Priced at $500 not
> the most economical option either.  Might just have the electrician put
> some
> parts together.
>
> --
> Regards,
> Mark Gouveia
>
> 2.7.4 Low Air Pressure Alarm Device
> Each dry pipe valve trim shall be provided with a local alarm device
> consisting of a metal enclosure containing an alarm horn or bell, silence
> switch, green power-on light, red low-air alarm light and amber trouble
> light. The alarm device shall be activated by the low air pressure switch.
> Upon reduction of sprinkler system pressure to approximately 10 psig above
> the dry valve trip point pressure, the low air pressure switch shall
> actuate the audible alarm device and a red low-air alarm light.
> Restoration of system pressure shall cause the low-air alarm light to be
> extinguished and the audible alarm to be silenced. An alarm silence switch
> shall be provided to silence the audible alarm. An amber trouble light
> shall be provided which will illuminate upon operation of the silence
> switch and shall be extinguished upon return to its normal position.
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)