That section is for Minimum Bolt Size for Concrete (9.1.3.10)

Trapeze hanger criteria is addressed in section 9.1.1.6. In your question, we 
find the answer in 9.1.1.6.7, "Holes for bolts shall not exceed 1/16 in greater 
than the diameter of the bolt."



Forest Wilson

Cherokee Fire


-----Original Message-----
From: Bobby Gillett <[email protected]>
To: [email protected]
Sent: Thu, Aug 27, 2009 9:42 am
Subject: All thread rod vs. bolts




Questionable issue:  NFPA 13, 2002 Edition: 9.1.3.10.2 Holes for bolts shall
not exceed 1/16 in. (1.6 mm) greater than the diameter of the bolt.  So here
is the question - is there a difference in between all thread rod and bolts
and is this 1/16" ruling meant for all thread rod also. (Can trapeze hangers
be slotted for all thread rod)?

 