Roland,

That's exactly what I meant.  In my opinion there would not be too many
times when a PS system would be advantageous when you consider the 50 psi
caveat.  I'm sure there are some cases but think they would be rare.

Cliff
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, August 27, 2009 10:23 AM
To: [email protected]
Subject: Re: Hydraulic Calculations

Just to ensure we clarify "for all intents and purpose"  I assume you  
mean the 50 psi caveat for systems greater than 5,000 sf kills the use  
of pipe schedule?  I ask since many inaccurately believe that PS is  
not ALLOWED beyond 5,000 SF.

Roland

On Aug 26, 2009, at 7:05 PM, Cliff Whitfield wrote:

> I don't think they were 'required' until sometime (I think '96) when  
> they
> took the pipe schedule option out of the standard (for all intents and
> purposes).  Until then, calcs were allowed but not required since  
> the pipe
> schedule system was still an option.  .
>
>
>
> Cliff
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to