Thom,

I think the platform is intentionally separated with a comma just for that
purpose.  If you look over in 11.2.3.1.4 "Restrictions" (3) specifically
addresses both 8.15.1.2 & 8.15.6.  I think it includes interior platforms.
Not sure why they gave it a separate heading and just didn't include it with
the concealed space items.

In reply to an earlier response, I don't think the presence of electrical
wiring constitutes a need for sprinklers in a space like this but the access
panels/doors certainly would.

Cliff

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, September 08, 2009 11:56 AM
To: [email protected]
Subject: RE: Church platform

8.15.1.1 Concealed Spaces Requiring Sprinkler Protection.
All concealed spaces enclosed wholly or partly by exposed
combustible construction shall be protected by sprinklers except
in concealed spaces where sprinklers are not required to
be installed by 8.15.1.2.1 through 8.15.1.2.16 and 8.15.6.

I love where the std can be used to Yeah and Nay at the same time. 

So where can we use the "Platform" exclusion. I say that this is a question
for the committee, but my personal position is that we need more info. I
believe that the "Platform generally referred to is an exterior loading
platform. I believe that your relying on the comma between the "Exterior
docks and platforms" Without the comma there is no confusion that the
platform is also exterior.

In your case it's an interior platform, so I would say 8.15.1.1 applies.
What is the construction of this platform? If you build it of "Composite
wood joist construction" You'd better sprinkler it, or you're looking at a
3000 SF design area above and below it. (If there is a below it.) If its
wood construction of any type and not fire rated, how is it not a concealed
combustible space?

8.15.6.1 Unless the requirements of 8.15.6.2 are met, sprinklers
shall be installed in spaces under all combustible ground
floors, exterior docks, and platforms.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, September 08, 2009 8:59 AM
To: [email protected]
Subject: RE: Church platform

And a height at which it would be tempting to store tables below it, etc. so
protection would be reqd- although leaving 18" clear above the spkrs would
be difficult to enforce past the design phase.

Also, if the church is using real alcohol vrs grape juice, the prev #13
reference asks if flammable liquids are handled above the platform or deck.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Tuesday, September 08, 2009 10:51 AM
To: [email protected]
Subject: RE: Church platform

I have done a couple of these both were under 30" off the floor, both had
access panels, and both had lots of wiring under them.  I didn't consider
using 8.15.6, due to the wiring and access panels.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]

-----Original Message-----
From: Cliff Whitfield [mailto:[email protected]]
Sent: Tuesday, September 08, 2009 7:34 AM
To: [email protected]; [email protected]
Subject: RE: Church platform

Todd,

 

Would this not fall under 8.15.6 "Spaces under Ground Floors, Exterior
Docks, and Platforms"?  If it met all of the requirements I would think you
could exclude heads under the platform.  Don't forget to apply the 3000 sf
remote area if you elect to not sprinkler that area.

 

Cliff Whitfield, SET

President

Fire Design, Inc.

 

[email protected]

www.fire-design.com

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________