Ok, this is from Findlandia Suana literature/ installation manual: 
(http://products.construction.com/Manufacturer/Finlandia-Sauna-Products-Inc-NST1770/products/Floor-Model-Electric-Sauna-Heaters-NST9534-P)

Note: When ordering, specify the elevation above sea level at your location. If 
a fire sprinkler is required, the head should be set at 275°F (or higher) and 
should not be located over the Sauna heater.



-----

There is also some guidance I found from Nordic Residential Fire Sprinkler 
Group: http://www.standard.no/Global/PDF/Standarder%20p%C3%A5%20h%C3%B8ring/294717.pdf



Their manual allows standard response in residential (which we don't).

But is also states that "Sprinklers installed in saunas shall have a temp 
rating close to but no lower than 30* C above the highest anticipated ambient 
temp."



The earlier post about maximum sauna temp being 195* is from UL 875 (according 
to the sauna website). I don't have a UL subscription so I can't verify that.

But, if maximum allowable temp is 195 F (90.55 C) , plus 30* C = 120.55* C 
(249* F).

So, using Eurpopean guideline the sprinkler would be 286* F maximum.









Forest Wilson

Project Manager
Cherokee Fire Protection Co.
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647


.



Visit our blog: www.cherokee-fire.blogspot.com 







NOTICE: The information contained in this email is intended to be solely for 
the use of the named individual or entity to which it is directed and may 
contain i
nformation that is privileged or otherwise confidential. It is not intended for 
transmission to, or receipt by, anyone other than the named addressee (or a 
person authorized to deliver it to the named addressee). It should not be 
copied or forwarded to any unauthorized persons. If you have received this 
electronic mail transmission in error, please delete it from your system 
without copying or forwarding it, and notify the sender of the error by reply 
email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll free.


-----Original Message-----
From: Ron Greenman <rongreen...@gmail.com>
To: sprinklerforum@firesprinkler.org
Sent: Sat, Sep 12, 2009 12:56 pm
Subject: Re: 13D Sauna/Steam Rooms



Sorry. I kept writing 286 but meant 360. I'm either getting old or am
lready there. I just can't remember which.
On Sat, Sep 12, 2009 at 9:47 AM, Thom McMahon <tmcma...@firetechinc.com> wrote:
 The maximum temp is a control setting the occupant can adjust. The emergency 
etting is typically higher. The one I looked at last summer was 250'F. Was it 
ettable to a lower temp.? I don't know it just said max temp. 250 on it.

 Yes 360 is high, but how many btu's to raise the ceiling temp to 360 from 194? 
ow long to set head off? Seconds! Yes the occupant could receive burns in those 
econds, but I doubt their blood could boil, unless you raised the temp 1 degree 
er minute or some such nonsense.

 286'F heads discharge to a fire located 30 or more feet below them in a half 
illion Sf bu
ilding in a couple of minutes. A 360'F head in a 1000 CF room will 
eact to a fire in seconds.

 We are fire protection, not slow electrical cooker protection. Life safety? 
orn strobe when temp exceeds 113'F, which I believe is the skin temp at which 
veryone feels pain.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926



 -----Original Message-----
 From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] 
n Behalf Of Forest Wilson
 Sent: Saturday, September 12, 2009 10:22 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: 13D Sauna/Steam Rooms


 From a website:

  maximum allowable sauna temperature in Canada and the United States is 194°F 
90°C). These are C.S.A. and U.L. standards set back in 1982. At that time, it 
as also mandated that there must be a high-temperature limit switch within the 
auna heater.

 ----

 Now, at 360*, in a 13D system, what is the priority: life or property 
reservation?

 At 360* in a very small room the person's blood must be close to boiling. 
ince the cut-off switch is a UL requirement, perhaps they have a paper on 
auna's with fire sprinklers.



 Forest Wilson

 Project Manager
 Cherokee Fire Protection Co.
 3195 Dayton Xenia Rd Ste 900
 Dayton OH 45434

 ph: 937-376-2333
 fx: 614-455-4324
 cell: 937-307-5647


 .



 Visit our blog: www.cherokee-fire.blogspot.com




=0
D

 NOTICE: The information contained in this email is intended to be solely for 
he use of the named individual or entity to which it is directed and may 
ontain information that is privileged or otherwise confidential. It is not 
ntended for transmission to, or receipt by, anyone other than the named 
ddressee (or a person authorized to deliver it to the named addressee). It 
hould not be copied or forwarded to any unauthorized persons. If you have 
eceived this electronic mail transmission in error, please delete it from your 
ystem without copying or forwarding it, and notify the sender of the error by 
eply email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll 
ree.


 -----Original Message-----
 From: Thom Mc
 Mahon <tmcma...@firetechinc.com>
 To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
 Sent: Sat, Sep 12, 2009 11:57 am
 Subject: RE: 13D Sauna/Steam Rooms



 This issue came up years ago while working with Jim Bell of Marriott Corp on 
e of their assisted living facilities a 13R that I have always used the ame 
ogic since then, and applied it to 13D as well. (1992) At that time arriott had 
bout 2 fires per year in sauna's, typically caused by bottles f body oil or 
owels placed over the heater. Jim's requirement was to prinkler all sauna's 
sing 300+ degree heads as the emergency cut out for auna controls is typically 
et in the high 200'F range. We currently nstall 360'F TYCO TY-B either 2.8K or 
.6K depending upon room size. (Yes=2
0I now they are STD response, but as we 
iscussed at the time, in a 8x10 room, ny protection is better than none, and 
td response Vs. QR will be a matter f only a second or two, with the ambient 
lready over 100'F.) 286'F heads re ok if your emergency cut off is set lower 
han 236'F, which I've never ound one that low. That's what we do and AHJ's only 
eed to hear this logic nce to accept it.
 Steam rooms, same source at Marriott, "What can burn? Tile walls, floors and 
iling, in a basic "Mist" system." Now Marriott used steel studs verywhere, so 
f your steam room is framed with wood and you have the steam enerator in the 
ypical under bench location, what we've done is put a head n that space, again 
igh temp. If the people or wet towels "s pontaneously ombust" in a steam room 
ot much a sprinkler can do to save them.
 I'd like to hear what others are thinking. 200'F heads will go off way too 
ten, 286'F may never go off if the emergency cut out is never needed, but  know 
hat if a 360'F head goes off, it's either a fire or mechanical amage.

 Thom McMahon, SET
 iretech, Inc.
 560 Copper Ridge Dr
 .O. Box 882136
 teamboat Springs, CO 80488
 el:  970-879-7952
 ax: 970-879-7926

 ----Original Message-----
 rom: sprinklerforum-boun...@firesprinkler.org
 mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Knight
 ent: Friday, September 11, 2009 4:33 PM
 o: sprinklerforum@firesprinkler.org
 ubject: 13D Sauna/Steam Rooms
 I am working o
n a 13D that has a sauna and steam room.  What temp sprinklers
 hould I use, and is it permissible to use QR instead of Residential?   I'm
 hinking that I will need high temp heads and residentials only go up to 75F, 
t least the ones that I'm familiar with.
 Thanks,
 Bob Knight, CET
 660 Hill Rd
 elba, Idaho 83641
 208) 318-3057
 208) 495-2057 fax
 o...@firebyknight.com
 ww.firebyknight.com
 -------------- next part --------------
 No virus found in this outgoing message.
 hecked by AVG - www.avg.com
 ersion: 8.5.409 / Virus Database: 270.13.91/2363 - Release Date: 09/11/09 
:15:00 _______________________________________________
 prinklerforum mailing list
 prinklerfo...@firesprinkler.org
 ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: supp...@firesprinkler.org To 
nsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 P
 ut the word unsubscribe in the subject field) 
_______________________________________________
 prinklerforum mailing list
 prinklerfo...@firesprinkler.org
 ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: supp...@firesprinkler.org To 
nsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 Put the word unsubscribe in the subject field)

 _______________________________________________
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:Sprink
lerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 _______________________________________________
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

-- 
on Greenman
nstructor
ire Protection Engineering
ates Technical College
acoma, WA
Member:
FPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
______________________________________________
prinklerforum mailing list
prinklerfo...@firesprinkler.org
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: supp...@firesprinkler.org
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to