IT is also worth  pointing out that after trying for 3 cycles to get  
ANYTHING in 13 indicating at what depth ( meaning distance down form  
the ceiling verses across the chord) a structural member IMPEDES heat  
so we can clearly say obstructed or unobstructed.  It is indeed 4  
inches.  See ROC 13-16.

So the determination depends on how far apart the purlins are and how  
deep they are and is now black and white.

Roland

On Sep 21, 2009, at 9:45 AM, Greg McGahan wrote:

> Has NFPA ever made a formal interpretation on whether purlins  
> construction is Obstructed or Non-obstructed construction?
>
> Thanks
>
> Greg McGahan