BUT

(A)    Where a vertical change in ceiling elevation within the area of coverage 
of the sprinkler creates a distance of more than 36 in. (914 mm) between the 
upper ceiling and the sprinkler deflector, a vertical plane extending down from 
the ceiling at the change in elevation shall be considered a wall for the 
purpose of sprinkler spacing as shown in Figure 8.6.4.1.1.3(A). 

According to the new rule I believe that we cannot use the obstruction rules.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bryan Dann
Sent: Wednesday, September 23, 2009 9:25 AM
To: [email protected]
Subject: RE: bar backs

Take a look at Figure 8.6.5.1(b)  page 13-57 NFPA 13(07)

If head can be 4'6 away from obstruction your ok.

Bryan A. Dann
Dannba Design Services, LLC
Fire Sprinkler Designs
Office: (740) 363-5878
Cell: (740) 803-0967
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, September 23, 2009 9:59 AM
To: [email protected]
Subject: bar backs


I have seen dozens if not hundreds of similar situation without sprinklers
and just wanted to get the professional spin on it:

The area behind a bar where the liquor is kept has a ceiling height of 9-6
and the remainder if the Bar is at 13'-0". Of course the "soffit" is about
1'-9" wide.

My thoughts are that a head is required due to the difference in elevation
being greater than 3'-0".

Any other thoughts?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to