Simply put, assuming you using push-on type joints for the underground, you rod 
from the base 90 up to the flange to keep the vertical piece in place.  The 
flange isn't moving so it holds it all together.

If the underground joint at the 90 used mega-lug or mechanical joints as it 
rose up to the flange at the floor then the rods between the base 90 and the 
riser flange are superfluous.

Check NFPA 24, 10.8.3 (2007) for the restrained joint details.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Tuesday, October 20, 2009 4:50 PM
To: '[email protected]'
Subject: RE: Retaining rod on UG-tangent

Geo.:

Are you saying these rods may not be necessary because of the restraint that 
may be present at the 90 deg. elbow below ground?  If so, what would be 
restraining the flange they're tying into (above the floor)?

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 1:10 PM
To: [email protected]
Subject: RE: Retaining rod on UG

And if there's already a megalug and/or thrust block on the 90 below, they're 
superfluous code-wise. Only need 1 of the 3 methods of joint restraint.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, October 20, 2009 2:00 PM
To: [email protected]
Subject: Re: Retaining rod on UG

Chris,
Sounds like the installer went to far more trouble than it was worth and may

have done damage in the process.The rod could have been left alone and 
connected to the flange by way of right angle "tie bolts".I have not found a 
restriction on welding the rod (we always used threaded rod couplings) and as 
for bending the rod,as long as you don't try to bend @ a 90 so as to break the 
core of the rod between the threads the inspector may not take any issue with 
it.But who knows,bending is bending.At least it isn't yours,since you are 
starting at the flange. Has the floor already been poured @ the run-in?

Lamar Vaughn
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to