Yea, I'm with Bob- we use Mega or Kwik flanges all the time without
incident. Guess Joe was right in waiting for a U Certificate :) LOL

And almost ANY device or method is subject to screwup when done wrong.
There's a grocery store chain around here that doesn't allow welded outlets
AT ALL. All mech tees (sigh). Must be a horror story there somewhere- cause
in the rest of the industry, we sure use a lot of welded outlets day in and
day out. Hm. Or at least- we used to !

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Tuesday, October 20, 2009 5:25 PM
To: [email protected]
Subject: RE: Retaining rod on UG-tangent

In my personal experience, except for Joe's example, haven't seen or heard
any horror stories of retainage flanges giving when properly installed.

BK

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, October 20, 2009 3:15 PM
To: [email protected]
Subject: RE: Retaining rod on UG-tangent

Out of curiosity, what is the performance report you guys have experienced
when using megalugs in this fashion without rods?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, October 20, 2009 4:05 PM
To: [email protected]
Subject: RE: Retaining rod on UG-tangent

Simply put, assuming you using push-on type joints for the underground, you
rod from the base 90 up to the flange to keep the vertical piece in place.
The flange isn't moving so it holds it all together.

If the underground joint at the 90 used mega-lug or mechanical joints as it
rose up to the flange at the floor then the rods between the base 90 and the
riser flange are superfluous.

Check NFPA 24, 10.8.3 (2007) for the restrained joint details.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Tuesday, October 20, 2009 4:50 PM
To: '[email protected]'
Subject: RE: Retaining rod on UG-tangent

Geo.:

Are you saying these rods may not be necessary because of the restraint that
may be present at the 90 deg. elbow below ground?  If so, what would be
restraining the flange they're tying into (above the floor)?

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 1:10 PM
To: [email protected]
Subject: RE: Retaining rod on UG

And if there's already a megalug and/or thrust block on the 90 below,
they're superfluous code-wise. Only need 1 of the 3 methods of joint
restraint.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, October 20, 2009 2:00 PM
To: [email protected]
Subject: Re: Retaining rod on UG

Chris,
Sounds like the installer went to far more trouble than it was worth and may

have done damage in the process.The rod could have been left alone and
connected to the flange by way of right angle "tie bolts".I have not found a
restriction on welding the rod (we always used threaded rod couplings) and
as for bending the rod,as long as you don't try to bend @ a 90 so as to
break the core of the rod between the threads the inspector may not take any
issue with it.But who knows,bending is bending.At least it isn't yours,since
you are starting at the flange. Has the floor already been poured @ the
run-in?

Lamar Vaughn
-------------- next part --------------

No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 8.5.422 / Virus Database: 270.14.23/2448 - Release Date: 10/20/09
10:43:00
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to