As long as the insulation is between the outside and your pipe you are OK with wet. You can't be in the insulation and you can't be on the cold side. The only exception I can think of is above coolers and freezers where the walls go to the deck. In these parts wet pipe will freeze unless they make some openings.
Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Forest Wilson Sent: Thursday, October 29, 2009 10:25 AM To: [email protected] Subject: guidance for piping above suspended ceiling / freezing Where is there guidance for acceptable piping above ceilings with wet systems? How does the sprinkler contractor know there will be sufficient heat above a suspended ceiling/ drywall ceiling to permit the use of water filled pipes? I understand that this is normally called for in specs. My question pertains to jobs where there are no specs. At what point is a dry pipe system/ other than wet option utilized? Forest Wilson Project Manager Cherokee Fire Protection Co. 3195 Dayton Xenia Rd Ste 900 Dayton OH 45434 ph: 937-376-2333 fx: 614-455-4324 cell: 937-307-5647 . Visit our blog: www.cherokee-fire.blogspot.com NOTICE: The information contained in this email is intended to be solely for the use of the named individual or entity to which it is directed and may contain information that is privileged or otherwise confidential. It is not intended for transmission to, or receipt by, anyone other than the named addressee (or a person authorized to deliver it to the named addressee). It should not be copied or forwarded to any unauthorized persons. If you have received this electronic mail transmission in error, please delete it from your system without copying or forwarding it, and notify the sender of the error by reply email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll free. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)