To my knowledge no Viking head was ever made with an O-ring. Also, heads with O-rings at the seat were not the problem. Those with O-rings in the waterway are the type that cause issues. And yes, there are other manufacturers with waterway O-rings but I'd rather not say who since that might imply they have issues and I have no knowledge of that.
On Mon, Nov 30, 2009 at 9:20 AM, Chris Cahill <[email protected]> wrote: > We've only been following the issue a little bit. I know about the recall > on Central heads so that's not the question. The question is - are there > other brands that are "rusting" and leaking from the seat? I've got a > Viking head from 1984 (might be a model XHH) that was leaking. It has a > flat cap much like the Central o-ring heads. It has a green "rust" line > around the seat. Is there other brands with o-ring, were they subject to > recall? Is the leaking caused by an o-ring, maybe I'm mixing two different > issues? > > > > Chris Cahill, P.E. > > Fire Protection Engineer > > Sentry Fire Protection, Inc. > > > > 763-658-4483 > > 763-658-4921 fax > > > > Email: [email protected] > > > > Mail: P.O. Box 69 > > Waverly, MN 55390 > > > > Location: 4439 Hwy 12 SW > > Waverly, MN 55390 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)