I think you're on the right track with at least an 8" lintel, but doubt that
in the ELO hazard, we can apply the residential 8" lintel as a solution.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Tuesday, December 01, 2009 2:50 PM
To: [email protected]
Subject: RE: QR / SR SPRINKLER SEPARATION 

But standard and qr cannot be mixed within the same compartment.
So I assume the question is definition of a compartment.

Forest Wilson Project Manager Cherokee Fire Protection Co. 1855 
Bellbrook Ave. Ste C
Xenia OH 45385
ph: 937-376-2333 fx: 614-455-4324 cell: 937-307-5647 . Visit our blog: 
www.cherokee-fire.blogspot.com NOTICE: The information contained in 
this email is intended to be solely for the use of the named individual 
or entity to which it is directed and may contain information that is 
privileged or otherwise confidential. It is not intended for 
transmission to, or receipt by, anyone other than the named addressee 
(or a person authorized to deliver it to the named addressee). It 
should not be copied or forwarded to any unauthorized persons. If you 
have received this electronic mail transmission in error, please delete 
it from your system without copying or forwarding it, and notify the 
sender of the error by reply email or by calling Cherokee Fire 
Protection Co. at 888-347-3079 toll free.


-----Original Message-----
From: George Church <[email protected]>
To: [email protected]
Sent: Tue, 1 Dec 2009 13:29:35 -0500
Subject: RE: QR / SR SPRINKLER SEPARATION

So you've just handed him the dilemma of using SR ELO's in a light 
hazard
corridor......hope people don't die.
:)
Seriously, Dwayne, I'd use the ELOs up the corridor and then switch to 
the
QR in the breakroom, assuming the breakroom is separated by a wall from 
the
high hazard area.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt 
Grise
Sent: Tuesday, December 01, 2009 1:20 PM
To: '[email protected]'
Subject: RE: QR / SR SPRINKLER SEPARATION

You must protect the lower hazard area at the higher hazard level for 
15'
beyond where the higher hazard ends.

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, December 01, 2009 12:17 PM
To: [email protected]
Subject: QR / SR SPRINKLER SEPARATION

I have an building where we go from an area that requires standard
response ELO sprinklers into a light hazard hallway and break room (QR
sprinklers) without any separation at the ceiling.  Is a draft curtain
required between the SR / QR sprinklers or are we ok since they are two
different hazards?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to