first off you are confusing the issue by stating 0.05 gpm/sf since  
these are not density/area sprinklers.  The 0.05 gpm/sf is a minimum  
flow but it is often exceeded by the listed require pressure for a  
evenly assigned rectangle.  AS in your case, the area for the 16 x 20  
is 320 requiring only 16 gpm for the non-criterion 0.05 density.  You  
identified the listing requires 22 gpm at 27.4 psi.  So where's the  
beef?

Roland

On Dec 8, 2009, at 7:38 AM, Todd Williams wrote:

> I am reviewing a set of plans where the designer used residential
> sidewall sprinklers in 13 system (6 story apartment bldg). A
> particular room is 18'6 x 12' and he has a sidewall throwing the 18'6
> and centered on the 12 ft wall. Since we have to use a 0.10 density,
> he based his design on 11.2.3.5.2. The listing for the sprinkler at
> the 0.05 density (16 x 20 sp) is 22 gpm at 27.4 psi. If we use the
> 0.10 density times the area as described per 8.5.2.1 (comment (2) in
> 11.2.3.5.2), we get 22.2 gpm at 27.9 psi. How can we expect to get
> twice the density at a an 18.5 ft distance out of the same flow and
> pressure by decreasing the width of a room?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to