No invoice, no opinion? :)

I don't think I'm wrong in stereotyping most sprinkler contractors as being
a bit myopic when it comes to the big picture and our cost relative to it.

Sure, most of our customers want to spend less- or nothing- on sprinklers.
HOWEVER, when the total system cost over the life of the building is
analyzed, upgrades may be cheaper than replacing the system or the
interference with operations that sprinkler problems can create- and I'm not
even addressing damage.

Am I correct that a little education is all that is necessary to convince
owners to stay the course of your upgrade, and buy peace of mind? I believe
it costs more to LIGHT the building over its life than it does to BUILD the
place. So while it looks like a lot when we're only looking at our pricing,
look at the big picture and understand why we're last trade bought out. 

When we've suggested design changes in DB work we were quickly educated that
while you can save a branchline per bay, the effect of a change in the steel
was a quantum increase in comparison to the paltry $ we were saving. 

If your work is 1~5% of construction, we'd have to be free to overcome a
change in building steel of only 5% of 38% of the building cost that steel
may represents.

Glc
Ps- I made up the 38% for steel as % of total building cost. Seemed close
enough for illustration purposes.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Scott A.
Futrell
Sent: Friday, December 11, 2009 11:34 AM
To: [email protected]
Subject: RE: tri seal gaskets

George,

I'm not Dave or Mark, and I don't have opinions (!), but the experiences are
bad with rusting (all the way through in less than 20 years) to freeze and
pipe separation - without flush seal gaskets.  We spec sch. 40 with cut
grooves, but get much negative feedback for conservative, more costly
approach.  Btw -7°F here this morning, but now it's +7!

Scott 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, December 11, 2009 10:18 AM
To: [email protected]
Subject: RE: tri seal gaskets

Before Frozen Dave became an SH wizard, he'd have chimed in here about the
"mini-dams" that get created when roll-grooved piping has condensation
puddling both in the pipe ends uphill from the groove intruding up into the
bottom of the pie, as well as the water sitting in the gasket. Potential for
corrosion and freeze/break. Not much we'll be doing about the puddling on
the bottom of the pipe, short of using Sch40 and cutgrooving (or thread it!)
but the area on the bottom of the coupling may be subject to a freeze/break.

Since he's native North Dakota, I'll defer to his expertise and experience
with cold far surpassing anything I'd tolerate before moving south.

Mark, you're entitled to an opinion on this and have remained in the same
tundra. Do you experience problems from liquids accumulating in these lower
areas? I can't ask Dave now, he'd suggest clean agent or Hi-Ex.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Denhardt
Sent: Friday, December 11, 2009 9:21 AM
To: [email protected]
Subject: RE: tri seal gaskets

Any gasket that is listed for dry pipe service may be used.  Most
manufacture's recommend using one but the other "less expensive" gaskets
are usually listed for dry pipe service.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Caputo
Sent: Tuesday, December 08, 2009 5:35 PM
To: [email protected]
Subject: RE: tri seal gaskets

Other than NFPA 13, section 6.5.3.3  "Grooved fittings, including
gaskets
used on dry-pipe, preaction, and deluge systems, shall be listed for dry
pipe service"  ?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Robert
Thompson
Sent: Tuesday, December 08, 2009 1:43 PM
To: [email protected]
Subject: tri seal gaskets

Is there a code that required couplings to have tri seal gaskets in dry
systems?
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email [email protected] 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to