We have a job where the residual pressure recorded during the backflow
test is lower than expected.  The hydrant used for the original water
test is about 10ft lower than the system riser and has a flow test
result of 72PSI static, 62PSI residual, flowing 902GPM (off a
circulating system).  I had my fitter install a pressure gauge before
the 1st check on the BFP and the we recorded a static of 67PSI but a
residual of 50PSI at a flow of 715GPM.  I confirmed with the water
utility that the gate valve for the water lead in is fully open and that
no pumps or valves have been shut off for water main breaks or
maintenance.  Unfortunately, they will not run a new flow test in
winter.
Any ideas as to what is causing the low residual pressure?  
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI