If you have a storage room defined by the EOR as a .222/2,000 remote area in the back of a retail store with NO separation to the retail area and you conform to both requirements (15' of the greater hazard and 30' of 286 deg heads) into the retail space:
Does this lock you out of changing to EC heads in the retail area if the EC head is listed as QR since you can't use the QR heads in the back? This is typical Beam and Purlin Construction and I would not consider a bay as a compartment. This really stinks if it is true, but am I right? Also, in A8.4 of the 2010 edition, it says "should" not shall for using SR and QR in the same compartment. Thanks as always for your input. Greg McGahan Operations Manager _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)