> On a more important matter: If a system was retrofitted with a backflow,
and
> there is no hydraulic calc plaque attached to the riser, and NFPA requires
> forward flow testing of backflows, how can you conduct the test without a
> benchmark to test against?
>
> What is the recommended practice in this scenario?
> Forest Wilson



>Add the cost of surveying and calcing the system to your bid.
> Ron



You are supposed to do this anyway.

See 8.16.4.6.2 (02 edition)

The annex goes on to mention schedule systems are not required to be
calculated, but the water supply still must be verified...

R/
Matt
 