I would sprinkle the entire attic an ember from the furnace could easily drift 
out of the limited coverage area. You might also look into putting up walls 
around the equipment. [that is just off the top of my head]

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Thursday, December 31, 2009 12:28 PM
To: [email protected]
Subject: 13R: Fuel Fired Equipment

Hello all,

NFPA #13R does not require the sprinkling of concealed combustible spaces 
except for when a few conditions exist one of them being when fuel fired 
equipment is located there. I have a project with wood open web trusses with a 
drop ceiling. Gas furnaces are located above the grid clg. Does this mean I 
have to sprinkle the entire attic or can I just put some localized coverage 
near the units? I didn't see anything in 'R' or the commentary that addresses 
this specifically.

Thanks,

RH






      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to