On the ones I designed, we used Antifreeze loop for the Collector (large
sucker, 14 ft long filter bags) with sidewalls installed on the plates
described previously. The interior ducting was protected with a Grecon spark
suppression system. This was for a large door knob production facility.
Might be a bit much for your type..?

R/
Matt
 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, January 07, 2010 10:42 AM
To: [email protected]
Subject: RE: Dust Ducts

Yeah, the flexheads with the adapter mounting plate for ducts works quite
well.  Makes inspection of the sprinklers simple with no need to disassemble
piping and drain systems. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jerry
Costello
Sent: Thursday, January 07, 2010 11:38 AM
To: [email protected]
Subject: RE: Dust Ducts

 Another suggestion, we have used "Flexheads" located in a removable 4"
sq plate. Makes install, inspection and replacement easier.


Jerry M Costello set
Advance Fire Protection
Ph 714-526-2231  Fax 562-691-5482

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Thursday, January 07, 2010 8:31 AM
To: [email protected]
Subject: Re: Dust Ducts

On the few (very few) school projects with dust collectors we have had to
design (not install mind you), we have provided details that sprinkler heads
would be installed in a "Tee" turned up with a cover plate to fasten the
sprinkler head and keep it positioned (include a union for removal).
Spacing of the heads were not to exceed 12' and only installed in ductwork
over 8".  An access door shall be provided at each sprinkler head location
in the main duct to access the head.  Heads were intermediate temperature
with corrosion resistant coating.  I believe we have also provided a dry
type head connected to the exterior dust collector hopper but my memory is
not going that far today with reliability.  That also would be a call by the
owner/AHJ since it's located outside the building and the level of
protection they want, in my opinion.

Hope this helps

Richard

On Wed, Jan 6, 2010 at 5:53 PM, Dennis Browning
<[email protected]>wrote:

> I have a High School with a Sawdust collection system that the 
> Building Department wants Sprinklered inside all ducts 10" and larger.

> Has anyone done this before and what about head/ abrasion problem?
Seems strange to me.
> What code would you design to for spacing, etc?
> Any input would help?
>
> Dennis Browning
> Browning Fire Protection
> Office # (541) 245-0466
> Fax #    (541) 245-0498
> Email: [email protected]
>  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to