All: 

Was this guide written to before or after the 13-D committee added the min 
gpm/sf requirement? 

Yours, 

Bruce Verhei 



----- Original Message ----- 
From: "Ron Greenman" <rongreen...@gmail.com> 
To: sprinklerforum@firesprinkler.org 
Sent: Thursday, January 14, 2010 3:49:02 PM GMT -08:00 US/Canada Pacific 
Subject: Re: Fire Departments - Inspection of residential systems faster, but 
just as sure... 

Or sadly, one of their children. 

On Thu, Jan 14, 2010 at 3:40 PM, Jim Johnston 
<j...@inlandfireprotection.com> wrote: 
> We had this very discussion at work yesterday. If Washington State were 
> actually successful in adopting the IRC as it reads I personally don't 
> believe there are enough sprinkler companies to do the work as conventional 
> (bid, design, permit, then install and test). We discussed how electricians 
> do residential work, I believe the 13D would have to follow suit, i.e. put 
> the heads where needed and follow up with a bucket test, if it doesn’t 
> produce the right flow put in an inline pump. We need to remember our 
> industry isn't an exact science, in college I designed machine tooling for a 
> production facility with .003" tolerances - that's nerve racking, we get to 
> work with feet and inches in the sprinkler industry - just don't exceed the 
> maximum spacing and produce the listed flows and pressures no problem. Most 
> of us that have been doing this for awhile know what pipe size we need - the 
> calcs are just a formality to prove our pipe sizes with the available water 
> supply. 
> 
> Ron, FYI the Commissioners for Yakima County have told the Fire Marshal's 
> Office that the sprinkler requirements will be exempt from homes and I 
> believe the Yakima City Council will do the same. We've got a lot of 
> experts out there making political decisions for the fire service - just 
> makes you wonder how people sleep at night maybe one of them will fall into 
> the 3000 annual fire deaths statistic? 
> 
> Jim Johnston, P.E. 
> Fire Protection Engineer 
> Inland Fire Protection, Inc 
> 1100 Ahtanum Road 
> Yakima, WA 98903 
> Phone 509-248-4471 
> Fax 509-248-1180 
> j...@inlandfireprotection.com 
> 
> 
> -----Original Message----- 
> From: Ron Greenman [mailto:rongreen...@gmail.com] 
> Sent: Thursday, January 14, 2010 3:00 PM 
> To: sprinklerforum@firesprinkler.org 
> Subject: Re: Fire Departments - Inspection of residential systems faster, 
> but just as sure... 
> 
> I reviewed this about ten years ago and I found the concept to be good 
> but there were many anomalies in the execution that put me off. I 
> don't recall what the exact issues were but the taste they left in my 
> mouth drove me back to 13D exclusively. On the other hand the rule of 
> thumb or schedule method in the 2009 IRC is not too bad. If I were an 
> AHJ I might consider letting owner builders do things per this method, 
> without the detailed plans, and then inspect the c**p (my favorite 
> word this week) out of them. As Scot points out electrical work in a 
> house is done without detailed plans and typically without load calcs 
> although they are required. In the case of house wiring the 
> prescription itself pretty much forces that the minimum be met. The 
> only true variables then are power supply (leads into the building are 
> sized appropriately) and the quality of workmanship. And for the rest 
> of you old guys, remember when we used to schedule major commercial 
> and industrial projects? We're talking houses here and houses are 
> something insurance companies don't even care about. 
> 
> On Thu, Jan 14, 2010 at 10:06 AM, Chris Cahill <chr...@sentryfiremn.com> 
> wrote: 
>> Good to remind all of this. I was not part of the development but did 
>> review it around that time. I found it to be rather good. The math was 
>> sound for the time. What I mean is this was before the 0.05 and the 
> modern 
>> crop of res heads so I can't swear the GPM and pressures are the same. 
>> 
>> Why it wasn't used more is two fold. First, there really wasn't much res 
>> sprinkler work at the time. This document was a little ahead of it's 
> time. 
>> Even today in the big picture there aren't many res sprinkler put in 
>> compared to the total SFH work. 
>> 
>> And second and most important was the fire marshals were very hesitant to 
>> accept. They wanted full detailed plans and HW calcs. I got very 
> negative 
>> feedback from those I introduced it to. Perhaps that is a positive in 
>> education and value done on 13 systems? I'd be curious to know since this 
>> was developed in MD and there are counties in MD that have been requiring 
>> SFH sprinklers do they use this in MD? How about AZ or GA or IL the other 
>> hotbeds for SFH sprinklers? 
>> 
>> 
>> Chris Cahill, P.E. 
>> Fire Protection Engineer 
>> Sentry Fire Protection, Inc. 
>> 
>> 763-658-4483 
>> 763-658-4921 fax 
>> 
>> Email: chr...@sentryfiremn.com 
>> 
>> Mail: P.O. Box 69 
>> Waverly, MN 55390 
>> 
>> Location: 4439 Hwy 12 SW 
>> Waverly, MN 55390 
>> 
>> -----Original Message----- 
>> From: sprinklerforum-boun...@firesprinkler.org 
>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... .... 
>> Sent: Thursday, January 14, 2010 11:51 AM 
>> To: sprinklerforum@firesprinkler.org 
>> Subject: Fire Departments - Inspection of residential systems faster, but 
>> just as sure... 
>> 
>> For jurisdictions facing budget 
>> cuts in their fire prevention departments, 
>> consider a document framed in 1995 by 
>> the US Fire Administration and conceived 
>> by Eric Schmidt, then FPE with Prince George's County 
>> Maryland. The 80 page document provides 
>> a method whereby residential sprinkler 
>> installation can be accomplished in a manner 
>> similar to how a journeyman electrician wires 
>> in electrical fixtures on a 20 Amp circuit... 
>> without plan submittal; simply an inspection. 
>> 
>> There are hydraulic calcs used to prove the system. 
>> But the method is so simplified that inspectors need not 
>> use Hazen-Williams. The method can 
>> eliminate sprinkler plan submittal for a deferred approval 
>> at inspection. A target-zone concept is used for sprinkler 
>> placement that allows for flexibility of field 
>> changes, while retaining assurance that supply still 
>> meets hydraulic demand. 
>> 
>> Jurisdictions interested in this significant time 
>> saving tool may find it through google at US 
>> Fire Administation's website using keywords: 
>> 
>> express residential sprinkler design guide US Fire Administration 
>> 
>> the downside is> 
>> designers make less money as there is no plan submittal 
>> the process is so easy even a plumber could attempt it ;-) 
>> 
>> the upside is> 
>> 1. fire departments use less time to approve residential 
>> sprinkler systems 
>> 2. fire department inspectors need only minimal amount of training 
>> 
>> This method might have been buried for 15 years, 
>> because it made the process -- too simple. It also 
>> might have been buried and forgotten for 15 years 
>> for reasons beyond my comprehension. I just mention 
>> it here in an attempt to get more sprinklers installed 
>> better and faster. 
>> 
>> 
>> scot deal 
>> excelsior fire 
>> _______________________________________________ 
>> Sprinklerforum mailing list 
>> Sprinklerforum@firesprinkler.org 
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
>> 
>> For Technical Assistance, send an email to: supp...@firesprinkler.org 
>> 
>> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
>> (Put the word unsubscribe in the subject field) 
>> 
>> _______________________________________________ 
>> Sprinklerforum mailing list 
>> Sprinklerforum@firesprinkler.org 
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
>> 
>> For Technical Assistance, send an email to: supp...@firesprinkler.org 
>> 
>> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
>> (Put the word unsubscribe in the subject field) 
>> 
> 
> 
> 
> -- 
> Ron Greenman 
> Instructor 
> Fire Protection Engineering 
> Bates Technical College 
> Tacoma, WA 
> 
> Member: 
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM 
> _______________________________________________ 
> Sprinklerforum mailing list 
> Sprinklerforum@firesprinkler.org 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: supp...@firesprinkler.org 
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
> (Put the word unsubscribe in the subject field) 
> 
> _______________________________________________ 
> Sprinklerforum mailing list 
> Sprinklerforum@firesprinkler.org 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> For Technical Assistance, send an email to: supp...@firesprinkler.org 
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
> (Put the word unsubscribe in the subject field) 
> 



-- 
Ron Greenman 
Instructor 
Fire Protection Engineering 
Bates Technical College 
Tacoma, WA 

Member: 
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM 
_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 

For Technical Assistance, send an email to: supp...@firesprinkler.org 

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to