I'll call to get a little more information on the situation (I'm doing
investigative work for someone else) and post again later on.

Thanks!


Carrol A. Glimstad
Fire Sprinkler Systems Designer

Cosco Fire Protection, Inc.
500 Menlo Drive, Suite 150
Rocklin, CA 95765
Ph:  916.652.1306
Fax: 916.652.1307
Email: [email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of tom
poisal
Sent: Friday, January 15, 2010 9:00 AM
To: [email protected]
Subject: Re: Sidewall with a 12" throwback?

Humm, your sooo close, 1" plus approx 1.5 to 2" to deflector, this is
existing right.  what is the width col to col?

On Fri, Jan 15, 2010 at 11:53 AM, Carrol Glimstad
<[email protected]>wrote:

> Branchline running 9" off back wall due to columns protruding into 
> room by 8".  I found a sidewall on Tyco's website, however, it appears
to be
> Norwegian, listed for some agencies that I do not recognize.   It did
> offer me a glimmer of hope that perhaps there was a listed (US) 
> counterpart.
>
>
> Carrol A. Glimstad
> Fire Sprinkler Systems Designer
>
> Cosco Fire Protection, Inc.
> 500 Menlo Drive, Suite 150
> Rocklin, CA 95765
> Ph:  916.652.1306
> Fax: 916.652.1307
> Email: [email protected]
>
>
>  -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of tom 
> poisal
> Sent: Friday, January 15, 2010 8:50 AM
> To: [email protected]
> Subject: Re: Sidewall with a 12" throwback?
>
> Carrol, I don't believe such a listing exists, what is your 
> installation configuration?
>
> On Thu, Jan 14, 2010 at 3:58 PM, Carrol Glimstad
> <[email protected]>wrote:
>
> > Does anyone know of a sidewall sprinkler that is listed for LH  with

> > an extended throwback?  Needs to cover at least 10 inches behind...
> >
> > Thanks,
> >
> > Carrol A. Glimstad
> > Fire Sprinkler Systems Designer
> >
> > Cosco Fire Protection, Inc.
> > 500 Menlo Drive, Suite 150
> > Rocklin, CA 95765
> > Ph:  916.652.1306
> > Fax: 916.652.1307
> > Email: [email protected]
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: 
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%3ASprinklerforum-requ
> > [email protected]>
> <to%3ASprinklerforum-reques
>  > [email protected]> (Put the word unsubscribe in the subject 
> field)
> >
>
>
>
> --
> Tom Poisal
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>



--
Tom Poisal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to