The commentary is discussing locating the pipe in the center of the hole,
not the penetration. I think you have to meet 9.3.4.2, or use the couplings.
9.3.4.4 substantiates, as well as 9.3.4.9.?? The couplings would be best
because of how much you would "rob" the structural integrity of the beam.


R/
Matt
 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, January 22, 2010 2:33 PM
To: [email protected]
Subject: beam penetrations & seismic. 

I ma working on a job where the engineer wants to run the mains 
through penetrations in steel beams. The question came up about 
clearance between the penetration and the pipe. Section 9.3.4 does 
not specifically address beams, but it is referenced in the handbook 
commentary under 9.3.4.1. Any thoughts on what minimum penetration 
size is required?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to