The scope of the data sheet in 1.0 says: 

"These recommendations do not conflict with internationally recognized
residential sprinkler standards (including NFPA 13D), except in the
matter of sprinkler density and design area."

It doesn't mention changing the water supply duration which is normally
10 minutes [or 7 minutes if a single story building and less than 2000
sq. ft.] per NFPA 13D.

I note that they require 60 minutes of water supply duration in 2.1.4.2:

"2.1.4.2 Ensure the sprinkler system is capable of supplying the total
system water demand for a minimum duration of 60 minutes."
 
It looks like this would negatively impact the cost of systems in rural
areas.




David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 