Since you are using large room it should not. If you were using area, you could not take the reduction.
R/ Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Monday, February 08, 2010 10:01 AM To: [email protected] Subject: mixing standard and QR spklrs in calc? I am working on a system for a school where the systems in some existing classrooms are going to be modified and all QR sprinklers are going to be installed. The hydraulic area I plan to use is one classroom of 4-6 sprinklers and two sprinklers in the corridor (meets requirements). The corridor sprinkler are standard response. That wouldn't effect the hydraulics in this situation would it? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)