2006 IBC/IFC

[F] 912.2 Location. With respect to hydrants, driveways, buildings and 
landscaping, fire department connections shall be so located that fire 
apparatus and hose connected to supply the system will not obstruct access to 
the buildings for other fire apparatus. The location of fire department 
connections shall be approved.

[F] 912.2.1 Visible location. Fire department connections shall be located on 
the street side of buildings, fully visible and recognizable from the street or 
nearest point of fire department vehicle access or as otherwise approved by the 
fire code official.

[F] 912.3 Access. Immediate access to fire department connections shall be 
maintained at all times and without obstruction by fences, bushes, trees, walls 
or any other object for a minimum of 3 feet (914 mm).

Hope that helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Monday, February 08, 2010 10:35 AM
To: [email protected]
Subject: RE: fdc clearance

Yes this does....thanks

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Letterman, Todd
Sent: Monday, February 08, 2010 9:28 AM
To: [email protected]
Subject: RE: fdc clearance

CFC 912.3 Access.
Immediate access to fire department connections shall be maintained at all 
times and without obstruction by fences, bushes, trees, walls or any other 
object for a minimum of 3 feet (914 mm). Nothing about electrical panels or gas 
meters, I guess it could be presumed.
NFPA 70 2) Outdoor. Outdoor electrical equipment shall be installed in suitable 
enclosures and shall be protected from accidental contact by unauthorized 
personnel, or by vehicular traffic, or by accidental spillage or leakage from 
piping systems. The working clearance space shall include the zone described in 
110.26(A). No architectural appurtenance or other equipment shall be located in 
this zone.

Table 110.26(A)(1) Working Spaces

 Nominal Voltage to Ground      Minimum Clear Distance 
Condition 1     Condition 2     Condition 3    
0-150   900 mm (3 ft)   900 mm (3 ft)   900 mm (3 ft)  
151-600 900 mm (3 ft)   1 m (3½ ft)     1.2 m (4 ft)   

Hope that is what you are looking for, you could also look in the National Gas 
Code for clearance on gas piping.

Todd Letterman
Fire Protection Engineer
Riverside County Fire Department
(951) 955-5273-Fax(951) 955-4886
[email protected]


-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]]
Sent: Thursday, February 04, 2010 1:43 PM
To: [email protected]
Subject: fdc clearance

Is there any written requirements to show the minimum distance the FDC has to 
be from electrical panels, gas meters, ect?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)




CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to