I need help before I make a mistake and insult a PE. Does anyone have recent 
experience in this area that can help with a few questions:

1) The Severity of the exposure per 80A
2) The meaning of the requirement to calculate ANY 300' section - I assume - 
but does it indeed mean even if there are multiple deluge systems on one side 
of the concourse that you must calculate 300 feet regardless so you would have 
multiple systems flowing in their entirety?

Just so you understand, this is an existing concourse with 2 deluge systems on 
each side. There are 36 nozzles (Viking C-1 window sprinklers) on one system 
calculated at 7 psi min per NFPA 13  througha 2" deluge valve and the system 
doesn't work by 200 psi. We are only supposed to be modifying the system and I 
did the calcs for proof for us. We obviously cannot participate in this game 
with such a deficit. 

AND if I have to include any 300' along the building and have to flow both of 
those deluge system simultaneously, well we are in serious trouble and I will 
have to explain this to people who don't know this subject.

Thanks for your help..