Cesar,

You will have to go by the listing for the sprinkler. If it is 
specifically listed for Light Hazard only, you can't use it for OH. 
If it is listed for use in NFPA 13 occupancies, it could be used in 
Light or Ordinary. The Tyco RFII can be used in on OH occupancy, such 
as a retail store. If you are talking extended coverage, that may be 
a different animal.


At 11:51 AM 2/16/2010, you wrote:

>Dear Forum Members,
>
>
>I apologise for my ignorance on the subject in reference but I do 
>have two questions regarding the use of sprinklers that I am 
>supposed to use for an area classifies as ordinary risk II:
>
>
>1. Could I use sprinklers "recommended" for LIGHT HAZARDS in areas 
>classified as ordinary risk?
>
>
>2. Why I can not find - from any manufacturer - Concealed Sprinklers 
>for the area classified as ordinary risk area?
>
>
>Any assistance will be highly appreciated.
>
>
>
>Rgds,
>
>
>
>Cesar Villavicencio
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to