Levent, Seems to me that developing a water supply for a standpipe system "in the middle of nowhere" will be far more expensive than doing the same for a sprinkler system, including the sprinkler system itself. The tank size and pump size can just be so much smaller in the latter scenario. There is also a huge leap of faith in believing that untrained personnel with hoses will get a fire under control before the arrival of the fire department. A total disaster is the more likely scenario. Of course we can only make recommendations and then try to solve the given problem as best we can, even if we know the performance criterion is wrong. It would be like being asked to design a sports car with wooden wheels and steel tires. It can be done, but it wouldn't work very well or for very long. I'd certainly put all my recommendations, based on generally accepted codes and practices in writing, and make sure they were included with any design I was directed to create that was based on user's poor specifications rather than on what I knew to be good practice. Buena suerte.
On Thu, Feb 18, 2010 at 7:55 AM, Ing. Levent Numanoglu <[email protected]> wrote: > Hello all once again and thank you for the valuable time and answers. Ron as > you mentioned, yes the prison facility and where my office is in Mexico but > I am in the city and the facility is in the middle of nowhere. > I will definitely discuss the points which you have outlined about the > evacuation plans. At this point the constructer is looking for a solution of > Fire Protection without sprinkler system, they definitely will not put a > sprinkler system its just going to be hose connections. So I am going > between the Class II and the Class III system. And the untrained personal > will have to use the standpipe - hose station in case of a fire as the FD > will probably arrive there after the fire is out. > > Ing.Levent Numanoglu > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Chris Cahill > Sent: jueves, 18 de febrero de 2010 08:56 a.m. > To: [email protected] > Subject: RE: Help > > True the code might give you guidance. But the more fundamental is who is > intended to use the standpipe. Untrained people - Class II, FD only - > Class I, either - Class III. And if it's FD the spacing, pressure and size > is up to them especially if not in USA. In other words maybe the FD would > like more pressure than they can normally provide. OK maybe not an issue > with a 2 story but who knows other than the FD and the designing > professional. > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ing. Levent > Numanoglu > Sent: Wednesday, February 17, 2010 6:38 PM > To: [email protected] > Subject: Help > > Hello all, > > > > I am trying to figure out which class of stand pipe system to use for a > multi detached building site. There are about 5 - 2 storey non-sprinkled > buildings from a single water supply from a clean water cistern. Each > building is supplied with a single standpipe in a central location within a > 100 feet away from the furthest point. Each building is a part of a prison > with individual cells. > > Any help would be greatly appreciated. > > Thanks, > > Levent > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)