2007 NFPA-14

6.4.5.4 Fire department connections shall be located not more than 100 ft
(30.5 m) from the nearest fire hydrant connected to an approved water
supply.

6.4.5.4.1 The location of the fire department connection shall be permitted
to exceed 100 ft (30.5 m) subject to the approval of the authority having
jurisdiction.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ether Barlow
Sent: Tuesday, February 23, 2010 8:40 AM
To: sprinklerforum
Subject: Fire Hydrants

I am wondering where ( if ) there is a specific code or requirement for the
FDC to be within 100' of a fire hydrant? I thought it was up to the local
fire department to make that call.................

-- 
My Thanks to You!

Ether J. Barlow, CET, NICET II
Manager/Fire Sprinkler Designer
The Tricom Group
(702)-383-2800x102 Phone
(702)-383-2806 Fax
(702)-491-1538 Cell
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to