NFPA 13 refers you to 409 (21.27, 2007) for aircraft hangers that are governed 
by 409.  If they are not governed by 409 then they are EH2 per 13.  If your 
hanger is subject to 409 then space according to 409 and you'll be fine since 
13 has no applicability.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ray Vance
Sent: Thursday, February 25, 2010 2:22 PM
To: [email protected]
Subject: Aircraft Hangar Question of the Day!

To my esteemed colleagues:

I have an aircraft hangar I am looking at and would like clarification on 
sprinkler / branchline spacing. I know what I think ;-) However, I would like 
the combined knowledge of all of you as to the actual requirements of the NFPA 
standards.

The hangar is a 32,000 suare feet Group-I hanger with a door opening to 
accomodate a 36 ft tail height.
The chosen fire protection scheme is Option-3, a closed-head wet-pipe sprinkler 
system at .17 gpm / 15,000 square feet and a low-level hi-ex foam system.
The building is a metal-purlin building with 25 ft bay spacing.

NFPA-409 requires a maximum 130 sf sprinkler spacing with a maximum distance of 
12 feet between the sprinklers or the branch-lines.
NFPA-409 does not reference NFPA-13 for sprinkler or branch-line spacing.

Question:

In a building with 25 ft bays would one be allowed to space the branch-lines at 
12'-6" as indicated in NFPA-13 for storage bays at 25 feet spacing in lieu of 
the 12 feet as indicated in NFPA-409?

Thanks,

Ray Vance - SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com<http://www.waynefire.com>
407-877-5563   office
321-436-2184   mobile

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to