Really?
Well I carried separate's for each valve.  I had originally posted about
these and the leaks we just could not find, even after flooding with 100 PSI
of water.  They're old central dpv's and we found leaks in the trim but
still had some others.  I'm using Victaulic dpv's with their amd trim
assemblies and will use a good gauge to set the downstream pressure.  So no
check between the tank and the amd's, just checks after the air shutoff at
each valve, cool.  I'm wondering about soft seat checks, not much around
here for brass seat checkvalves anymore, most are imported with plastic
trimmed seats.  Same for renewable seat shutoffs, wondering about ball
valves instead.  Could I omit the relief if the tank is only at 90 and the
system at 13?
Tom


a single air maintenance device will serve multiple systems properly 
isolated from each other with check valves.



Thom,

Try to think of the whole thing as a system. Compressor pumps into
tank through a check valve and the tank itself is extended through
some piping to a system (or more) made up of more of the tank in a
funny shape that resembles a sprinkler system. Because you want the
air in the sprinky part to be different than the air (pressurewise of
course-not chemical make-up) you need a check valve to separate the
two. If you have multiple sprinky parts you need air maintenance and
check for each. You don't need to trap the air between the compressor
check and the tank outlet from the supply pipe.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to