Stewart,

Thank you for the response.  A client of mine had an accidental Inergen
dump which coincided with immediate, massive hard drive failures in
their facility.  Do you know of any issues specific to Inergen?

On a side note, I've specified FM-200 several times thinking it was a
good option for data centers but if there is a corrosive by-product it
doesn't sound like a good choice in these situations.  I would like your
citation to review.  What do you typically specify for data centers?  Do
you have any experience with NOVEC 1230?

Jeff DuBois, P.E.
Fire Protection Engineer
Spectrum Engineers, Inc.
E-mail: [email protected]
Direct Phone:  801-401-8496
Fax: 801-401-9496


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Stewart
Kidd
Sent: Friday, March 05, 2010 8:12 AM
To: [email protected]
Subject: Re: Clean agent questions

Can't comment on whether drives are sealed but when FM200 is discharged
during a fire it produces a residue which is corrosive - let me know if
you want a citation for this.

Stewart Kidd
On 5 Mar 2010, at 13:27, <[email protected]> <[email protected]>
wrote:

> They do leave some residue but they shouldn't have any affect on hard
drives.  Hard drives are supposed to be hermetically sealed.
> 
> 
> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
> 
> 
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of DuBois,
Jeffrey D.
> Sent: Thursday, March 04, 2010 6:34 PM
> To: [email protected]
> Subject: Clean agent questions
> 
> Long time lurker, first time poster.
> 
> I'm wondering if any of you have any experience or knowledge of FM-200
or Inergen systems affecting hard drives in a data center after a system
dump.  Are these systems really harmless to the equipment as the
manufacturers claim?  Do they really leave no traces behind afterward?
> Please contact me off forum with any information.  Thanks.
> 
> Jeff DuBois, P.E.
> 
> Spectrum Engineers, Inc.
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to