For the same reason that they accept the Hyd. Calc programs output you send
them.FDT has the resources of the world's largest behind it, what have you
got backing up the last hand calc you did?

The math is too out there for any of us to follow, and since I've heard of
the results for trips vs. calc for this program is very, very close, from
the examples they've done, who would you rather have behind this product
than TYCO? Barney and Bills Fluid get there in the right time software?

http://www.sprinkcad.com/sprinkfdt.php 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, March 11, 2010 2:31 PM
To: [email protected]
Subject: RE: DRY SYSTEMS FOR DUMMIES

Sorry to be a pessimist, but why would a AHJ buy off on this calculated time
delivery versus seeing the real thing?  I can think of a number of instances
that the owner of this software has messed up before.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc