Every winter in this land of the midwest, I see at least one dry pipe system 
that has tripped because someone disconnected the air supply.  The most common 
problem is a "permanent" air compressor installation powered through an 
ordinary toggle switch and someone flipped the switch thinking it operated the 
lights.  The air leaks out of the system over hours or days to the trip point 
of the DPV.  The valve trips, fills the system with water, it freezes and 
bursts pipe and/or fittings.  Of course, there are usually other issues like 
missing or improperly installed, tested and maintained air supervision and 
alarm devices.  The result is a flood.  The cost of such a flood can be large.
 
My advice:  hard pipe and hard wire the compressor into the system.  If the 
electrician insists on a toggle switch (Ron, since you have 70 handy, is a 
disconnect switch within sight of the motor a requirement if it is a fractional 
HP motor?), then make sure it is away from the door to the room where it might 
be mistaken for the light switch.  I like to see the switch installed at 6' AFF 
and directly above the air compressor.  The switch should also have a sign 
stating "Air Compressor for Sprinkler System -- DO NOT SHUT OFF" or something 
similar.  One of those switch guards that minimizes the chance of accidentally 
bumping the switch to the off position is a good idea too.  The circuit breaker 
for that circuit should also be labeled and have a lock provided by the breaker 
mfr. (compatible with the breaker so that the breaker can still operate) to 
keep it in the on position.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 3/18/10, Ron Greenman <[email protected]> wrote:


From: Ron Greenman <[email protected]>
Subject: Re: Hard wired air compressors
To: [email protected]
Date: Thursday, March 18, 2010, 1:59 PM


Weel, back to what I just found in 70 then if it were disconnected
when you look at it it is an impairment. When you plug it back in and
verify it operates properly it is not.

On Thu, Mar 18, 2010 at 11:49 AM, Ron Greenman <[email protected]> wrote:
> As I look through the electric code an argument could be made that a
> plug is not what would define portable or permanent. In fact an
> argument could be made that even a quick-disconnect air line in
> addition to the plug could still be considered permanent and that the
> term "permanent" has more to do with how the compressor is used than
> how it is installed. So if it's mine and I say it's permanent, even
> with a plug and a quick disconnect, then it's permanent no matter what
> you suspect my intentions are. Now this is based on your quoted text
> from 13 and NFPA 70 422.30-422.33.
>
> On Thu, Mar 18, 2010 at 11:19 AM, Greg McGahan <[email protected]> wrote:
>> Ok, what about the argument that it is hard piped and even though it is 
>> plugged in you can't pick it up and remove it?
>>
>> Greg McGahan
>>
>> Living Water Fire Protection
>> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Ron Greenman
>> Sent: Thursday, March 18, 2010 1:18 PM
>> To: [email protected]
>> Subject: Re: Hard wired air compressors
>>
>> Yes to discussed before and I agree with your interpretation.
>>
>> On Thu, Mar 18, 2010 at 11:16 AM, Greg McGahan <[email protected]> 
>> wrote:
>>> This is a friendly discussion and not a conflict. However, please see
>>> the interpretation below.
>>>
>>>
>>>
>>> 13-7.2.6.2.1 states, the air supply shall be from a source available at
>>> all times.  A plug-in air compressor is portable and would not meet the
>>> 'all times' criteria.  Hence, my interpretation that the compressor
>>> would have to be hard wired.
>>>
>>>
>>>
>>> Has this been discussed previously?
>>>
>>>
>>>
>>> Thanks
>>>
>>>
>>>
>>>
>>>
>>> Greg McGahan
>>>
>>> Operations Manager
>>>
>>>
>>>
>>> Living Water Fire Protection
>>>
>>> 1160 McKenzie Road
>>>
>>> P.O. Box 877
>>>
>>> Cantonment, Florida 32533
>>>
>>> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>>
>>> [email protected] <mailto:[email protected]>
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to