I think this is exactly what I needed. 

As always, I can not tell you how much I appreciate this forum and the sharing 
of intel. Some of you guys are the bomb.


Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Sunday, March 21, 2010 12:10 PM
To: [email protected]
Subject: Re: Fire Pump Transfer Switch

I presume Tom's inability to look up sections is due to his not being
near his books rather than because he was captured by marauding
Hittites, had his eyes puts out, and then sent to the mines of
Anatolia. That being said I have books and owe him a favor so here is
text from 110/2005 that I believe supports the "the wires have to be
there" argument and though I didn't look it up I know the separate
conduits for control and feeder wires is correct also.

(4)     Manually operated (test) switch located in each automatic
transfer switch (ATS) that simulates a loss of power and causes
automatic starting and operation until this switch is reset, to cause
the engine circuit to duplicate its functions in the same manner
commercial power is restored after a true commercial power failure.

Note the test switch is to be in the ATS while the starter controls
for the generator have to be at the generator location (and this is
directly stated in 110 as well as 70. Not what the electrician or the
GC want to hear but you might explain it that as the pump is analogous
to a heart would he want his emergency heart fixing glycerine pills in
his pocket or back home in the medicine cabinet?

On Sun, Mar 21, 2010 at 8:18 AM, Tom Duross <[email protected]> wrote:
> The basic principal behind the switch is to start the genset when loss of
> power is detected and then transfer.  Without the start wires, it cannot
> start the generator.  This is a constant problem in new startups because the
> designers/engineers forget this.  Not uncommon for me.  Also, the wires
> cannot be run in the same conduit as the emergency feeders.  20 requires
> independent control of the generator whether type 1 or 2 arrangement.  I
> can't look up the sections but they're in there.
> Tom
>
>
> I have looked in 70 and 20 and in the archives but I cannot find the
> requirement (at least where I can understand it) that "control wires" are
> required to run from the transfer switch to the emergency generator.
>
> There are not such wires on the Electrical Drawings and hence no wires were
> installed and the FP is 500' from the Genset. The GC is trying to prove to
> the owner why this should not be an issue for the Electrician but should
> have been on the Electrical drawings since it is required by code and is
> necessary for the proper transfer switch operation.
>
> The only thing I can find is in 20 10.8.3.6.2 and 10.8.3.13 (momentary
> switch to simulate loss of power). I think maybe the wires that are not
> there involve the momentary switch but I honestly do not know.
>
> If you can point me in the right direction it would help us help a friend
> and I would really appreciate it.
>
> Greg McGahan
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________