Chris, I've used and specified nitrogen without problems especially as a backup for dry and special hazard systems. Agree with Ron that the biggest problem is making sure the cylinders are replaced. John D. provided some information on nitrogen generation systems (that are spendy), but yet another option.
Scott Futrell (763) 425-1001 Office (612) 759-5556 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Friday, March 26, 2010 8:48 AM To: [email protected] Subject: Nitrogen I was under the impression we talked about nitrogen in dry systems was a challenge because it leaked where plain air would not. I searched the last few years of the forum and couldn't find any such discussion. But air is 80% nitrogen so maybe not a significant difference? How many of you have tried nitrogen and did you or do you still have leaking problems? Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)