A "listed" component is one that has been tested and found to meet to
its specified measure of performance by a 3rd party agency that is
qualified to undertake such analysis and that is approved by the AHJ.
In the past, I've had badge-heavy fire officials tell me that they only
"approve" UL listings, but none could or would ever answer my follow-up
question, "Based on what criteria?".   In fact, FM is a well-regarded
and diligent testing lab that has been more conservative with certain
listings over the years than U.L. (I'm thinking of the years when they
wouldn't list concealed sprinklers for Ordinary Hazard occupancies, for
example.)   Contrary to popular misunderstanding, there is nothing in
any NFPA standard that requires a product to be U.L. listed, only
listed.   There are quite a few products out there that carry either
U.L., or FM but not both; the obvious reason being the cost of the
testing and listing services.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Denhardt
Sent: Thursday, April 01, 2010 11:44 AM
To: [email protected]
Subject: RE: UL/FM approvals

No, you can use it on any job where the AHJ considers FM to be an
acceptable approval agency.  99.00% of AHJ will gladly accept FM.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Thursday, April 01, 2010 2:59 PM
To: [email protected]
Subject: UL/FM approvals

We found a flexible sprinkler drop that carries the FM approval but is
not
UL listed. Does this mean I can only use it on FM jobs? 

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to