Forumites,

NFPA 20 - 2007 par. 5.7.6.2 ( = 2010 par. 4.7.7.2)  says:
"Pressure relief valves and pressure regulating devices in the fire 
pump installation shall not be used as a means to meet the 
requirements of 5.7.6.1." (= 2010 par. 4.7.7.1)

I ask this question because it seems to be not unusual in my country 
to fit fire pumps with a pressure relief valve to limit the churn 
pressure below 175 psi in systems that need a high pressure (e.g. 165 
psi) in the point of operation. Thus flattening the first part of the 
curve up to the point of operation.
This happens to both, engine driven as well as electric driven fire pumps.
In engine driven pumps they use for this purpose the same relief 
valve as mentioned in section 5.18 "Relief Valves for Centrifugal 
Pumps" (= 2010 section 4.18).

Can anyone tell me why this par. 5.7.6.2 says: "shall not be used" ?
Why did the committee put this in the code ?
I remember times when it was not in there.
Is this based on bad experiences?

When I point other technicians to this rule a common response is "Why 
? We do it all the time! "

Can anyone of you shed some light on this issue?

Frans Stoop
TOS architecture & fire protection
Netherlands <f.st...@tosfire.com>
Tel. +31-24-324 0112  