Tyco RSV-1 (1") size, they used to make a 2" and you may still find one on somebody's storage shelf. Be careful the lit says for use in 13D systems. You may need to look at a solenoid valve on the domestic operated from the flow sw.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matt Grise Sent: Thursday, April 08, 2010 3:39 PM To: '[email protected]' Subject: RE: FM Small Room Rule? Is anyone familiar with a product that automatically shuts of the domestic water in a combined sprinkler system? I am working on a retrofit system for an apartment building (that was severely damaged by fire) and it only has a 1.5" copper line coming into it. I think I can get it to carry the sprinkler system, but there is no way that it can support the sprinks and domestic load. 13R (2002 -6.5.5) says that "domestic demand shall be included... ...where no provisions are made to prevent the domestic water flow upon sprinkler system activation" Any recommendations or successes with provisions to prevent domestic water flow? Thanks! Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)