Charles ,
 The AHJ can require new calculations if you are reducing pipe size . In your 
case you are increasing the end piece which always tends to balance the head 
flows more efficiently.This should actually make the system better.JMHO
 BTW , make sure you are using the same type of pipe.


---- John Drucker <[email protected]> wrote: 
> 2002 NFPA-13 
> 
> 14.1.2 Deviation from approved plans shall require permission of the
> authority having jurisdiction.
> 
> 14.4.4.5 Friction Loss. Pipe friction loss shall be calculated in accordance
> with the Hazen-Williams formula with C values from Table 14.4.4.5, as
> follows:
> (1) Include pipe, fittings, and devices such as valves, meters, flow
> switches in pipes 2 in. or less in size, and strainers, and calculate
> elevation changes that affect the sprinkler discharge.
> 
> John Drucker, CET
> Fire Protection Subcode Official 
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, May 11, 2010 5:09 PM
> To: [email protected]; [email protected]
> Subject: RE: Pipe Size
> 
> If you change pipe sizes, then yes you'd have to recalc.  That's pretty much
> a given since your system hydraulics can change and you'll have no idea of
> the overall affect on the system performance.
> 
> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SCĀ  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Charles
> Thurston
> Sent: Tuesday, May 11, 2010 4:32 PM
> To: sprinklerforum
> Subject: Pipe Size
> 
> Hello All you Fine folks of the Sprinklerforum,
> 
> I am looking at replacing all the pipe in a 2 story parking deck  due to
> external corrosion (The fitters will love to be to look at the beach while
> they "work"). 3" main fed from a 500 GMP ??PSI pump. The building the pump
> feeds is 16 stories of  condos. 
> 
> 
> Each branch line feeds 5 heads now.
>  1 1/4" from main feeds heads 1-4 and 1" to the 5th head. It will be cheaper
> to run the branch line all the way out in 1 1/4 fitting and machine
> adjustment wise. The AHJ "ask" if it was allowable to change the pipe size
> without re-calcing the entire system. It is planned to measure out the pipe
> lengths and out the heads back in the same locations. I have not found
> anything in NFPA 13 2007 addressing this. Does anybody know a reason not to
> run 1 1/4" all the way out other than to "balance the flow" in the last
> head.
> 
> -- 
> Best regards,
>  Charles Thurston                          mailto:[email protected]
>   Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
>   AFAA Guest
> 
> Electronic Privacy Notice:
> This e-mail, and any attachments, contains information that is, or may  
> be, covered by electronic communications privacy laws, and is also  
> confidential and proprietary in nature. If you are not the intended  
> recipient, please be advised that you are legally prohibited from  
> retaining, using, copying, distributing, or otherwise disclosing this  
> information in any manner. Instead, please reply to the sender that  
> you have received this communication in error, and then immediately  
> delete it. Thank you in advance for your cooperation
> 
> 
> 
> 
> 
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.18, Virus/Spyware Database: 6.14970)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to