Greg ,

 If this is a full protection 13 system , you may delete this protection under 
certain conditions , keeping in mind you may have to provide 3000 sq.ft. design 
areas in the occupied spaces above if you do.
 If it is a 13R system , this area would not require protection anyway .

Lamar Vaughn , SET

---- Greg Lindholm <[email protected]> wrote: 
> I have an Architect that just called to ask about whether or not he would 
> have to extend sprinkler protection to a combustible crawl space below an 
> assisted living facility. 16" open web wood joists with 8" of insulation at 
> the top of the space, and about 8" from the bottom of the joists to the 
> ground.
> 
> I told him that off the top of my head, I would say that he would need 
> sprinkler protection there, "but" I don't think I have ever put sprinklers in 
> a space like this. (It would be impossible to maintain if anything happened 
> down there.)
> 
> Anybody's thoughts?
> 
> Greg Lindholm