Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)


At 08:23 AM 5/19/2010, you wrote:
>I'd ask him to please, for your edification, cite the sections of 
>the NFPA Standard where he derived his specification data.
>
>I guess he was looking at sprinkler data sheets and when it didn't 
>say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft 
>he thinks it falls into that category?
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Wednesday, May 19, 2010 6:11 AM
>To: [email protected]
>Subject: 13R sprinklers
>
>I am working on a project with a rather ignorant engineer who will
>not accept listed flow requirements for residential sprinklers. He is
>insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
>flow and 18 for single sprinkler flow (we have to calculate both). My
>question may be one of semantics, but this is what the engineer is
>hanging everything on. Both the above spacing and discharge
>requirements are under sections entitled "Sprinklers That Have Not
>Been Listed with Specific (Discharge/Coverage) Criteria". Since
>virtually all of the residential sprinklers I am aware of have
>specific design and coverage criteria, am I to assume based on the
>wording that sprinklers with specific criteria cannot be used under
>this section? If so, are there any sprinklers without specific
>criteria currently on the market?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to