At first blush this is not a good idea. You could develop a head pressure water 
column above the DPV which can slow or even prevent operation of the DPV. Newer 
DPV have a low differential. You still need expansion tank $$. How do you do a 
trip test AF then air then water. No No No!
Sent on the Sprint® Now Network from my BlackBerry®

-----Original Message-----
From: Vince Sabolik <[email protected]>
Date: Thu, 20 May 2010 11:46:40 
To: <[email protected]>
Subject: RE: Ant-Freeze Systems

So now I'm wondering why this is OK but the NFPA frowns on trapped 
water in a heated
area in a dry system.


At 11:42 AM 5/20/2010, you wrote:
>So the idea would be that when the anti-freeze system activates, the 
>antifreeze solution would be blown out by the supervisory air, then 
>the dry valve would trip, then the water would fill the system and discharge?

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to