Note the doors aer large enough to wheel in 55 gallon drums of gasoline, so
why not require dikes and .6? Might turn into flammable liquid storage some
day, they SHOULD have a 250,000 gallon tank and 1500 GPM pump, or PCD!!!

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Friday, May 21, 2010 8:52 AM
To: [email protected]
Subject: RE: Occupant load vs Square footage

You only have 2 exits. One really cause that is where all people go. (the
door they came in) I have seen this several times. Sounds like it is still
an assembly, it is just limited to 45. Empathize with the owner while
providing the cost of the sprinkler system.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Owen Evans
> >Sent: Thursday, May 20, 2010 8:50 PM
> >To: [email protected]
> >Subject: Occupant load vs Square footage
> >
> >Here's the situation:
> >
> >
> >A person wants to open up a martial arts studio in a strip mall. The
> >middle unit has 2800 square feet of open floor space for matting. The
> >building dept. comes up with an occupant load of greater than 50 people
> >therefor, it is classed an assembly. The planning dept. gave the business
> >a C.U.P for an occupant load of 45 people because of limited parking.
> >
> >
> >Here is the rub. In Redondo Beach if there is a change of occupancy to an
> >assembly fire sprinklers must be provided. Yes thats right, fire
> >sprinklers. According to the building dept. the business must run a fire
> >service to the middle unit in an otherwise unsprinklered strip mall.
> >
> >
> >Even though the planning dept is only allowing an occupant load of 45 the
> >building dept is stating that because the unit COULD be used as an
> >assembly, it must be called an assembly and therefor requires fire
> >sprinklers. The owner is REALLY upset.
> >
> >
> >To me this is UNREASONABLE and I am trying to help the business owner
> >avoid the fire sprinklers.
> >
> >
> >Any input on how to approach this would be appreciated.
> >
> >
> >Regards,
> >Owen Evans
> >
> >
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.819 / Virus Database: 271.1.1/2883 - Release Date: 05/20/10
> >01:26:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to