I would be concerned with NOT protecting the area under the 2' wide
plywood , can't think of any exception that would allow you to not have
protection , and because of the 3' depth you will have to have heads
under the enclose. My 2 cents worth.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Thursday, May 27, 2010 2:47 PM
To: [email protected]
Subject: Beam obstructions

I have a crawlspace that has to be sprinklered. I need to get exact
measurements, but for now I'm guessing it is about 4 feet high. The
plywood
ceiling of the crawlspace tight to the bottom of main floor joists is
smooth
& flat. The problem is the crawlspace has "utilidors", enclosed heated
spaces for running ducts, piping etc. Generally, these utilidors,
encased
with plywood, are 2 feet wide (horizontal) and about 3 feet high
(vertical)and run everywhere in the crawlspace, with no set pattern.
Think
of the utilidors as wood beams coming down from the ceiling. I will have
sprinklers inside the udilidors if they are not filled up with ducts or
piping. My question is there is about a foot of space below the
utilidors.
My opinion is it should be okay if I space the heads on both sides of
the
obstruction complying with 13(2007) section 8.6.5.1.2 (2) and not
provide
additional heads below the obstruction. Any dissenting thoughts?

Tony 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to