Todd ,

Is this a vertical "in-line" pump taking suction from a municipal supply or a 
vertical turbine which will have a shaft down in a reservoir or wet pit ? If it 
is the latter the pressures will vary above the former.

LV

---- Todd Williams <[email protected]> wrote: 
> I'm more sizing a pump for bidding than drawing it at this point . 
> I'm not of what pump will be used, so I'm nervous about using 
> specific curves. The flows on this job are about 300 gpm and I'm 
> using a 500 gpm pump. Most of the VT pumps I've used have demands 
> greater than the rated flow. Think I'll play it safe and assume 120%.
> 
> 
> 
> At 02:52 PM 6/3/2010, you wrote:
> >Todd:
> >
> >140 is the maximum allowed, but most pumps that I've encounter -
> >horizontal and vertical - are closer to 120% of rating at churn.   But
> >definitely go to the data sheets because many curves are steeper than
> >others ...
> >
> >Steve Leyton
> >Protection Design & Consulting
> >San Diego, CA
> >
> >
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Michael
> >Gallello
> >Sent: Thursday, June 03, 2010 11:51 AM
> >To: [email protected]
> >Subject: RE: vertical pump - theory vs reality
> >
> >140% is the NFPA throw at it if I remember correctly.  I've never gone
> >with the 120/140 or whatever that NFPA "suggests".  Size your pump, pick
> >one, check out the performance curve from the manufacturer.  Tada.  ;-)
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Todd
> >Williams
> >Sent: Thursday, June 03, 2010 2:48 PM
> >To: [email protected]
> >Subject: vertical pump - theory vs reality
> >
> >I am designing a system with a vertical turbine pump. When figuring
> >churn pressure, is 140% of rated match what happens in reality? My
> >design has low flow, but high pressure.
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >
> >__________ Information from ESET NOD32 Antivirus, version of virus
> >signature database 5170 (20100603) __________
> >
> >The message was checked by ESET NOD32 Antivirus.
> >
> >http://www.eset.com
> >
> >
> >
> >__________ Information from ESET NOD32 Antivirus, version of virus
> >signature database 5170 (20100603) __________
> >
> >The message was checked by ESET NOD32 Antivirus.
> >
> >http://www.eset.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to