NFPA 11 (2005) section 4.7.2.5 says black steel piping in foam solution piping 
is to be 100.  No delineation is made as to the type of system.  Hence, I've 
been specifying worst case of 100.

NFPA 11(2010) section 4.7.2.5 states only the requirements for galvanized foam 
solution piping and refers back to NFPA 13 for other C-values.  NFPA 13 (2010) 
table 22 4.4.7 indicates C of 120 allowable for deluge systems such as those 
feeding foam systems.  Also, NFPA 13 (2010) section 12.11.1 states to install 
in accordance with NFPA 11.  Seems a bit circular.

Anyone know the reason for the change?  Am I interpreting it correctly?