I got a loading dock in a freezer.  It's open to an area of 25' rack
storage.  All plastics, including exposed small totes.  The HPS design is
rather straight forward.  My issue is the loading dock.  Would one normally
call a loading dock storage in accordance with '02 ch 12?  It's too large an
area to call misc storage because of the 4,000 sq.ft. (it is under 10% of
the building).  

 

Normally the question doesn't make a difference.  But in this case I have a
35' building.  So 5' in a 35' building causes 12.2.3.1.5.2 design for 20'
clear.  Thus I look at the plastics table and have a 0.85/2600 density
(15'/35', group A, non-expanded, exposed).   And because it is open to the
racks I get to carry this density over the racks for 15' which should make
the balancing of the in-racks fun.   Did I mention this is an existing
situation?  Probably can make it work with the existing supply.  But will
need to tear out the whole thing including the PA valve and protecto wire. 

 

This is where the code seems to take me.  Any suggestions on is this right
or a better way to look at it that doesn't get this costly?  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 